Excitation of Pressure Transducer using Voltage Module NI-9201
Hello, I hope everyone is healthy and well. I am a beginner in designing measurement systems. I am trying to measure the pressure, temperature and flow of a liquid that is flowing through a pipeline. There will be a pump in the circuit and maximum pressure in system will be 15 bar.
I am using Honeywell MIP Series Pressure Transducer has a linear relationship between measured pressure and output voltage. The output voltage of sensor is between 0.5V and 4.5V. This sensor must be excited by 5V. Since I need to read the voltage measurement, I am planning to use NI-9201. Does this voltage input module have a capability of exciting the specified pressure transducer?
Best Regards.
(2,214 Views)
Accepted by jiyanbaran
I've ony done a quick look, so do check to confirm before doing anything:
  • The term "excitation" voltage, usually implies a sesnsor with some sort of bridge arrangement, but looking at the MIP datasheet it just looks like the 5VDC is just a regular power supply to the sensor.
  • You can use the NI-9201 for the pressure signal connection, but it cannot provide the power supply to the sensor and you will need to provide that externally to the IO module.
  • There are some AI modules that can provide power supply lines to sensors, but they tend to be the AI current modules for 4-20mA signals. There is a good white paper on Field Instrument Wiring that is useful if just learning about the many different ways that sensors can be wired to IO modules - though that is more about noise, single ended vs differential - rather than power supply to sensors - https://www.ni.com/en-gb/support/documentation/supplemental/06/field-wiring-and-noise-considerations...
Consultant Control Engineer
www-isc-ltd.com
(2,179 Views)
Hello Sir,
Thanks a lot for clarification.
Best Regards.
Jiyan Baran Bukun
(2,135 Views)