11-03-2006 12:03 PM
11-03-2006 03:25 PM
11-05-2006 11:00 PM - edited 11-05-2006 11:00 PM
I am not sure since I have not tried it out, but I think that shorting terminals might make you read the cjc value for that channel instead of 0 deg.
One way I did was to program a logic to detect all open TC channels in the read data ( they would be reading a saturated value at around max or min set for that cahnnel) and then, I would use array operations to replace that channel's data with an array of 0's
Message Edited by devchander on 11-05-2006 11:02 PM
11-06-2006 10:36 AM
11-07-2006 12:21 AM
Malay, guess you posted the wrong link. It brings you back to this page itself
Here is the link which I guess, Malay intended to post
And what I have observed is this: In SCXI 1102/B/C modules, open thermocouple detection circuit enables you to scan across open TC channels in your scan list without measurement errors, but it does not bring the open thermocouple channel's read value to 0 deg C/F
11-07-2006 10:28 AM
Hi,
The open thermocouple detection knowledge base did the trick.
Thank you all for the help!
11-07-2006 05:54 PM
11-10-2006 03:30 AM