Counter/Timer
NI 9411 and Linear Encoder - Inverted travel
I've stumbled across an issue with two NI-9411s being used in a NI-9149 c-RIO to measure linear motion.  Each 9411 is used one at a time and they are reporting encoder output differently.  Here's the scenario:
1 - cRio chassis is being used
1 - quadrature encoder
1 - LabVIEW program
1 - DUT.
When I have 9411 - "A" plugged into the c-RIO and connected to encoder, the test item travel is reported as increasing.
When I remove 9411 - "A" and plug 9411-"B" into the c-RIO, connect the exact same encoder to it, and move the DUT through the same travel motion, the travel is reported as decreasing.
The c-RIO and 9411's are brand new.
Is there a setting on the card that could have been changed somewhere, a bad card, or something else possibly?
Any insight would be helpful.
Thanks!
(1,673 Views)
Hi Dakota,
Sounds like an interesting problem.  Are you placing 9411-A and 9411-B in exactly the same slot of the 9149 chassis?  If so, given that everything else about the system is the same (ex: same LabVIEW code, same PC, etc.), then the results from the 2 modules should be the same.  Also be sure to check the wiring for both of your modules is exactly the same, as the A and B phases may be swapped for the 2nd module, causing the reverse in direction.
BR
John
Add motion to LabVIEW in 30min or less - TENET EMotion
Finding it hard to source NI hardware? Try NI Trading Post
(1,652 Views)
John,
Yes, everything about the test system is exactly the same with the exception of the NI 9411 module.  I was utilizing one test system and just swapping the 9411s out.  Ended up sending the module back to NI for evaluation.
Thanks!