Slide Switches on FBUS-HSE/H1

Hi, I was wondering if the slide switches that are on the bottom
of the FBUS-HSE/H1 (near the part number label) did anything
useful like clearing non-volatile RAM, etc...
 
They are not mentioned in the manual. 
 
Thanks.
0 Kudos
Message 1 of 4
(7,112 Views)
The switch at the right is used to reset the linking device and the other 2 switches are reserved for the future use. Please refer to the attached file (Appendix A Resetting FBUS-HSE/H1 LD, and Figure A-1) for the details.

帖子被fieldbus在01-03-2007 12:19 AM时编辑过了

0 Kudos
Message 2 of 4
(7,106 Views)
I tried the procedure described in Appendix A of the FBUS-HSE/H1 LD User Manual to reset the device and the
Ethernet STATUS LED never flashed, indicating a device reset (per Table B-1).  
 
The switch seems to have no effect.
0 Kudos
Message 3 of 4
(7,060 Views)
Thanks a lot for your report! Would you please try the software way to verify the reset operation?

After the reset, please run Interface Configuration Utility or NI-FBUS Configurator. If the existing configurations (the most obvious example is the device tag) are cleared, it means the reset takes effect.
0 Kudos
Message 4 of 4