Eric,
One FP-1000 (or FP-1001/160X/20XX) can control up to 9 IO modules. If the second FP-AO-210 is not being detected by FieldPoint Explorer there are a couple things to check. First check to make sure that all of the terminal bases and modules are firmly connected to each other.
Next, check the Power & Ready LED of the FP-AO-210 at address 2. Both LEDs should be lit. If they are not, de-power the system, remove the modules and terminal bases and make sure that you do not have any bent pins. Re-assemble and power up the system. Use FieldPoint Explorer again.
If the module is still not detected, take a look at the addressing of the detected modules. The system should be detecting the first FP-AO-210 at address 1 (or 1 + a multiple of 10 if you have s
et the FP-1000 to a different address). If the FP-AO-210 is at a different address, then it is likely a problem with the addressing circuitry either in the network module or the terminal base. Try swapping the positions of the two terminal bases and try again. If it works, then the error is in the addressing circuitry of the terminal base, if not, then it is in the addressing circuitry of the network module. Note: bent pins can also cause this.
Regards,
Aaron
LabVIEW Champion, CLA, CPI