Justin,
Your answer is slightly misleading. The OPC Server resides on the host computer and is part of the NI-FieldPoint installation. When you use DataSockets to browse to the OPC Items that were configured via NI-FieldPoint, you are configuring the system to use the OPC Server that resides on the host computer and not on the cFP controller. The FP and cFP controllers do not have OPC Servers built into them. The host computer (NI-FieldPoint Server and OPC Server) communicates with the cFP system via the NI ethernet protocol.
DataSocket, in addition to communicating via OPC, DSTP, HTTP and FTP can also communicate using the NI Ethernet protocol. In this way, you can actually use DataSocket to speak directly to the cFP module as described in the fo
llowing KnowledgeBase Article. http://zone.ni.com/devzone/conceptd.nsf/webmain/A6617392B393C4B886256ACB0053AEBE?opendocument
Regards,
Aaron
LabVIEW Champion, CLA, CPI