‎12-22-2005 10:17 AM
Hi Soup-
I do not see that behavior; I am testing with a FP ethernet module and a FP-TC-120. The array returned from the FP Read is consistent with the data for all channels. What hardware are you testing with?
Thanks-
‎12-27-2005 04:01 PM
‎12-27-2005 05:05 PM - edited ‎12-27-2005 05:05 PM
Message Edited by Tom W [DE] on 12-27-2005 05:08 PM
‎12-27-2005 05:05 PM - edited ‎12-27-2005 05:05 PM
Message Edited by Tom W [DE] on 12-27-2005 05:07 PM
‎12-27-2005 05:07 PM
‎12-27-2005 05:17 PM
‎12-27-2005 05:33 PM
Hi Soup-
I have noticed in testing that if any channel is out of range the "All" channel readings are all zeros. Can you confirm from MAX whether the Status readings for each channel indicate that any channels are out of range? If so, a simple range adjustment my be able to remove the zero'd channels problem.
‎12-27-2005 05:50 PM
‎12-27-2005 06:05 PM
Hi Soup-
To clarify then, is the "first" AI module returning good data in LabVIEW when you read the "All" channel? It sounds like it is working properly in MAX. I would suggest shorting the other channels or setting them to a range that will not be out of range when they're left disconnected. This should let you scan the "All" channel without it returning zeroes due to the out of range error.
‎12-27-2005 06:11 PM
No, the first FP-AI-110 module and the FP-AO-200 module both read 'Successful' for all the channels singularly, as well as the "All" line item, but I still get all zeroes when I try to read these modules with the "All" Item Name.