Modbus TCP & Starting Address

Hi!

 

What is this "Ex" at the left border of the second line? Exception?

Modbus is able to return error messages.Those contain the original adress and the original function code + 0x80 as well as an error number.

 

That is, it seems your device indeed speaks ModbusTCP, and responds with a valid error message. At least, it seems so from your screenshot.

Not every software handles error packets correctly, and since nor normal answer package is sent, runs into a timeout.

 

Click on those lines, and  wireshark will show you a very detailed analysis of the packet in the lower half of the window.

It's possible it also shows you the error message as text.

 

0 Kudos
Message 11 of 12
(476 Views)

Hi Sebastian,

 

Yes, Exception : Gateway path unavailable.

 

So does it mean that my gateway can be the problem ?

Because I'm doing : Computer --> Gateway --> Chamber.

I've seen that : "Usually means the gateway is misconfigured or overloaded."

I don't really know what to do now...

 

Thank you