Communicating with an Allen-Bradley ComapctLogix processor over Ethenet

What are the requirements for communicating between Lookout and an AB CompactLogix PLC?
 
The communication will be Ethernet to the Compactlogix PLC.
 
This is an existing application where Lookout communicates to an Automation Direct PLC via Ethernet.
 
We are adding a new AB Compactlogix PLC to the system.
0 Kudos
Message 1 of 4
(5,126 Views)
Lookout doesn't have built-in driver for CompactLogix PLC.
You need to use 3rd party OPC Server, such as RSLinx. Lookout can act as OPC Client.
Ryan Shi
National Instruments
0 Kudos
Message 2 of 4
(5,120 Views)
Does Lookout 5.1 support OPC?
 
IF it does, then we would need RSLinx OEM, that has OPC.
 
Thanks for your help.
0 Kudos
Message 3 of 4
(5,113 Views)
Yes, Lookout 5.1 has OPC client object to connect OPC server. It's opc 1.0 and 2.0 compliant.
Ryan Shi
National Instruments