Lookout
Garbled communication response from Modbus secondary(9):Incorrect Secondary Response
While performing single register writes to a SCADAPack PLC using Modbus RTU protocol, I  consistently recieve
"Garbled communication response from Modbus secondary(9):Incorrect Secondary Response"  and the communications fails.
The serial port diagnostic file is as follows:
18:39:11.5 - Station5_RTU ->
[05][06][00][C8][00][00][09][B0]
Station5_RTU - RTS low
18:39:11.7 - Station5_RTU <-
[05][03][16][01][0B][00][00][00][00][00][00][00][00][00][00][00][00][00][00][00][00][00][00][02][C9][5E][C7]
I have tried changes to the Modbus.ini file with no successful results.
Any hints would be greatly appreciated.
David
(4,009 Views)
Do you have any other software that can communicate with this PLC by Modbus RTU protocol?
If yes, you can compare the sent/received codes and find something difference.
Ryan Shi
(3,986 Views)
It looks like your diagnostic file is only logging the responses and
not the requests, since 05,06,... is either a request or response to a
function 6 (single register write, of register 40201 or 200 depending
on your numbering system), and 05,03,16,... is definitely a response
to a function 3 (multiple register read of 11 registers).
Try using Modbus Test Pro to talk to the ScadaPack to ensure the
ScadaPack is configured properly, and not acting as a Modbus Master
rather than a Modbus Slave. There is also a possibility that the
requested function 6 register is not a valid register on the
ScadaPack.
The ScadaPack is actually one of the devices we use to test Modbus
Test Pro against. Download it for free (shareware) at
http://www.rawiq.com/mbtestpro.php
Hope this helps!
Tim Kirk
tkirk@rogue-engr.com
www.rogue-engr.com
(3,952 Views)