11-12-2012 10:37 PM
I am new to NI-DAQ. I run a sample code provided by NI in Visual C++ from "\National Instruments\NI-DAQ\Examples\DAQmx ANSI C\Analog In\Measure Voltage\Cont Acq-Int Clk".
I am supplying 10HZ sinusoid from function generator, it gets the signal, but it starts to increase signal, i.e. acquired sinusoid moves slowly from -2.5V : 2.5V to 5V-10V.
KY
11-13-2012 04:27 AM - edited 11-13-2012 04:27 AM
Seems that you source (generator) is really floating 😉
Since the DAQ input outputs a tiny current (input bias current) you need to provide a current path to A(in)GND. Have a look at the DAQ input connections diagrams in the DAQmx manual.
Usually a resistor (100k?) from Ai- to AGND will provide a bias current path and fix the signal (and your problem).
11-13-2012 06:17 AM
Thank you very much, I have already tired it before, but my problem was that the input terminal configuration for the AI channel was set to default (DAQmx_Val_Cfg_Default)
and by default it uses Differential mode (DAQmx_Val_Diff), whereas Referenced single-ended mode(DAQmx_Val_RSE) was required.
Hope it will help others...
Khassan from Kazakhstan