i have a hardware and electronic question, and hope anyone can help me with advice:
We are controlling the speed of a motor with a 0 to +10 V Analog Output Signal of a DAQ device. (The AO is connected with a motor controller). The controller is not very reliably and it happens that it regenerates voltage peaks of 60 V and transients which could destroy the Input of the DAQ.
The question: How can I protect the AO? My idea was to build in into the circuit a schottky-diode (Current only in direction of controller) and a TVS-diode which cuts all peaks. Please see the attached draft.
Would that be a good enough, or which is the usual stuff to solve this problem?
I also have a little problem to select a correct TVS diode, because I don´t understand what the characteristics like the
"Maximum reverse standoff voltage" and "Breakdown voltage" mean. So how should the characteristics of the diode be? (The signal is only from 0 to +10 V, so anything above theese limits can be eliminated with a shortcut...
Thanx all for your replies!!
(3,269 Views)
here is a quick idea
R3, D2, V2 form the motor controller with a 60 spike, V1 is AO
Since you have a 0-10V output a simple zener would do the job. I choose a 12V type
R1 and R2 limit currents and protect the diode and the AO.
If your controller have a low input impedance the voltage drop over R1, R2  have to be regarded. A test would answer that question 🙂
However the current the AO sink still could be 12mA ...
Maybe the output is already clamped, and all what is needed is a current limiting resistor? That is a question only NI can answer.
I'm a fan of LTspice, simple and fast. Starting LV and LTspice at the same time, this circuit was ready while LV still was loading 😉
(To be honest, the circuit yes, but the parameter where still missing)
Greetings from Germany
Henrik
LV since v3.1
(3,262 Views)
Hi Henrik,
thanx for your reply! If I understood you correctly, the only component you would build in for protection is the zener-diode which shortcuts all negative spikes (Higher than 0,7 V) and all positive spikes above the +12 V level? R3, D2, V2 only simulates the spikes, is that correct?
You wrote:
"If your controller have a low input impedance the voltage drop over R1, R2  have to be regarded. A test would answer that question"
I am not an expert in electronics. How can i find that out? Our controller is a prototype...can that be simply tested with the "Ohm-function" of a multimeter? I know that the current which flows into the controller is not more than 10 mA...
What is the purpose of R1 and R2? Don´t they have an impact on my signal?
Thank you again, greetings Markus
(3,254 Views)
R1 and R2 limit the currents in case of spikes.
R2 limit the current for the protecting zener to I(D1) = ( U(spike=V2) -U(zener=12V) ) / R2
R1 limit the current into the AO . Assume the worst case U(AO)=0V then the current it has to sink is ( U(zener)-U(AO) ) / R1= 12mA
If the input of the motor controller form a Ri= 10k input impedance you build a voltage divider
and the controller will see a voltage of Ui=U(AO) * Ri / (R1+R2+Ri)
You apply 10V at the AO and the controller will only see 8.3V , however if the input impedance is 100k the controller will see 9.8V
Henrik
LV since v3.1
(3,249 Views)