robo rio 2.0 wont boot out of box, checked against other rio's that boot fine
03-24-2023 10:15 PM
Hello frc1027,
Can you please elaborate on the behavior you are seeing with your roboRIO 2.0 and the steps you have tried so far?
Have you followed the imaging procedure, as well as the recommendations in this document: FRC roboRIO STATUS LED Constantly Flashing ?
Thanks,
04-14-2023 09:30 AM
hi, we have received a RoboRio 2.0 at the start of the 2023 frc season, and out of the box the rio would not boot/load. we strongly believe it is a faulty rio as we are able to swap different rios lent to us by other teams and they work fine, we've tried all recommendations we can find but nothing works. as a result we had to rely entirely on devices lent to us.
the rios we used in place were the same model as the one we ordered and we were able to succeed with our standard protocol when using a different device. Even Robot inspectors had concluded that it is a fault in the Rio and suggested we RMA the device.
04-14-2023 09:38 AM - edited 04-14-2023 09:39 AM
Please start a new thread for seperate issues. This helps to avoid confusion on which teams have tried what.
One note, a lot of teams have gotten tripped up on getting device to image properly,
Make sure to image the SD card using the .img.zip file with either BalenaEtcher or the Raspberry Pi imager as described here: https://docs.wpilib.org/en/stable/docs/zero-to-robot/step-3/roborio2-imaging.html
04-14-2023 10:09 AM
this is the same issue just still unresolved, we have the have used the correct imaging files in the sd card. this has been ruled out and tested for by several different people at several different times.
the only remaining possibilities is that the rio is faulty, or has gained sentience and decided to go on strike for better working conditions.
04-14-2023 11:53 AM
Ah, I should have checked the username on the original post.
roboRIO units are tested before they leave manufacturing. What is the behavior you see when attempting to power the device? no lights? solid red power? flashing status?
04-14-2023 12:32 PM
we get a solid red power light.
04-14-2023 12:39 PM
Thank you.
A solid red power light means the device has detected a short and entered safe mode. We've had a few teams report having units do this on arival.
Please open the device using the four screws on the back and the two screws at the port port and clean the circuit board off using compressed air. (Maybe also use a flashlight to inspect the board closely for any remaining metal shards or other foreign materials and remove them as well.)
04-14-2023 01:05 PM
weve actually already had this suggested to us and have done so, we have not seen any change since doing so
04-14-2023 01:34 PM
I've sent you a private message with next steps.