Repeat Scans Using DAQmx Read/Write
Accepted by AlfredoT
Alfredo,
I've rearranged your DAQmx code a bit, though I can't test it, but it should show what I have in mind.
Dan
Message 11 of 23
(2,422 Views)
Thank you Dan!
It works perfectly. I'll study the little changes you made in order to understand them and keep them in mind next time I'm programming something similar.
Alfredo
Message 12 of 23
(2,416 Views)
Jeff,
I remember why I've grown used to using a shift register with DAQmx tasks... The pesky for loop which iterates zero times.  If I remember correctly output terminals from such a for loop place default data on the wires... not good if you had a task with reserved resources wired into the loop!  However this is unnecessary in this case, as a while loop was used. Your point about the additional overhead incurred in this case is a good one!
Dan
Message 13 of 23
(2,415 Views)
Alfredo,
One quick correction to the VI I posted.  I think you'll want to change "ai/sampleClock" string constant to read "ai/startTrigger".
Dan
Message 14 of 23
(2,410 Views)
I noticed that too but don't know what difference it will make.
Alfredo
Message 15 of 23
(2,408 Views)
Dan:
I just made the change and tested it but I get an error message and the scan gets hung up. I'll leave it at sampleClock because it is working that way.
Alfredo
Alfredo
Message 16 of 23
(2,403 Views)
Alfredo,
In your case, the fix would start the AO task just a bit sooner.  I'm not sure what hardware you're running this with, but what typically happens is the following:
1) Start trigger is issued in DAQmx Start Task for your analog input task.
2) A short delay occurs.
3) A sample clock is issued to begin the acquisition of the 1st sample.
Explanation of Step 2:
For most devices (assuming E Series, M Series, X Series or S Series), the short delay (step 2) is by default two ticks of a 20 MHz (or for X Series, 100 MHz) timebase.  However, users can increase this delay pragmatically via the DAQmx Trigger->Start->More->Delay property.  This would increase the amount of time between the AI Start Trigger and the first sample clock.
I suspect your goal is to start AI and AO at the same time.  With my original VI (ai/sampleClock), the signal which triggered your analog output would be the first sample clock.  This signal is subject to the delay I described above.  When you specify ai/StartTrigger, your analog input task will export the start pulse which will not be delayed as described above.
I hope that explanation is clear.  Please let me know if you have additional questions.
Dan
Message 17 of 23
(2,402 Views)
Alfredo,
Out of curiosity, what error did you see when you used ai/startTrigger?
Dan
Message 18 of 23
(2,394 Views)
@Mcdan wrote:
Jeff,
Dan
Well reasoned- And valid although, while loops must iterate at least onceSmiley Happy if you can reproduce the benchmarks posted later in the "Sean" thread I would be interested- there were a lot of background processes on the machine I used and the results were not difinitive.
Message 19 of 23
(2,392 Views)
Jeff,
Are you referring to the benchmark VI you posted here?  If so, I'll have a go at it when I get a free moment or two.  If you have another benchmark in mind, please point me to it.
Dan
Message 20 of 23
(2,390 Views)
