Multifunction DAQ
How to generate a short pulse output with a hardware timed analog input
I have a DAQPAD 6070E (so I have to use traditional NI-DAQ). I acquire data using AI Single Scan, so that I can do a hardware timed acquisition. On the output side, I would like to generate a 4 Volt output signal, that I can drop to zero for a brief time (less than 1 microsecond), and then bring the output voltage back up to 4 Volts. I would drop the voltage once approximately every 100 msec. My analog input runs at a scan rate of 20,000 Samples/sec.
Is there a way to generate this short drop on an analog output line? Am I limited to doing an analog output at 20,000 samples/sec because of my analog input hardware timing requirements?
Any help and suggestions would be greatly appreciated.
Thanks.
(2,931 Views)
The from looking at the Product Data Sheet for the max analog output rate on the DAQPad 6070E and I found it to be 1 MS/s, so that means you can have 1 us down and 1 us back up in theory. I checked the slew rate on that device and found that it is 20V/us, so you shouldn't have a problem with actually dropping down 4V and then back up 4V.
It should be possible to use a rate faster than 20 kHz for Analog Output, but even with that, your total pulse duration will be 2 us.
If you need something faster than that you might be able to invert some of the Generate Single Pulse VIs, which can have a resolution of 2/(Clock Rate) for your pulse. However, doing so will give you a 5V signal instead of a 4V signal.
(2,921 Views)