11-26-2012 06:50 AM
I have a NiDAQ 9188 connected to a PC via ethernet. All of the modules are visible in MAX and check out OK but if I try to connect using OPC, I can only see one item "ServerPollingRate". Is there something I need to do to get the NI OPC server to pubish the channels?
This is my first time with the 9188, I have used compact fieldpoint expansion chassis many times before without any trouble.
Solved! Go to Solution.
11-28-2012 07:04 AM
Hey,
Are you running an NI OPC server on the PC? What are you trying to read with/ publish to?
It would be useful to have a system diagram or description, and what you have done so far in terms of setting up.
Here is a pretty good overview of how to set up OPC with DAQmx, it might have the answers you are looking for.
http://www.ni.com/white-paper/3742/en
11-28-2012 07:36 AM
Ian,
Thanks for the link to the overview document. I wasn't aware that I needed to define shared variables for the channels. Now that I have done that I can read the channels via OPC.
Thanks for your help.
Tony
11-28-2012 07:46 AM
No problem, glad I we could resolve the issue